(28 intermediate revisions by 2 users not shown)
<div style="background-color: #FF2A2A; border:2px solid #FF0000; color: black; font-weight: bold; text-align: center; padding: 2px;">This page is in a work in progress, the informations here can be modified any time. Please, do not edit it yet, check the discussion section if you'd like to contribute with.</div>
<div style="background-color: #FF2A2A; border:2px solid #FF0000; color: black; font-weight: bold; text-align: center; padding: 2px;">This page is a work in progress, the informations here can be modified any time. Do not rely on the content of this page.</div>
== About ==
== About ==
Control Chain is an open hardware assignment protocol developed to reflect the LV2 controls properties. In other words the Control Chain able you to control LV2 plugins control ports using a hardware device like Arduino.
Although the Control Chain has been created focused on MOD, it isn't a must to has it working with LV2 plugins. This can be done using, for example, an Arduino, connected via USB to your PC.
This page concentrates technical informations of Control Chain. If you are looking for startup guide to create new controllers, please refer to MOD Arduino Shield article, there you will find a tutorial and Arduino cases that will help you.
This page concentrates technical information of Control Chain. If you are looking for a startup guide to create new controllers, please refer to [[MOD Arduino Shield]] article, there you will find a tutorial and Arduino cases that will help you.
== Physical interface ==
Line 74: Line 74:
The '''destination''' and '''origin''' fields are addresses that says from where the message is going to and coming from, respectively. The value '''0x00''' stands for the host address and the devices addresses values must be between '''0x80''' and '''0xFF''', inclusively. The '''check''' is the byte message verification. It's calculated XOR'ing all message bytes.
Size fields marked with ''1B_str'' stands for a string started with one byte, that indicates your size, and followed by your data characters. For example, the "hello" string will be represented by:
{| class="wikitable"
| 0x05
| h
| e
| l
| l
| o
=== Commands ===
=== Commands ===
Line 102: Line 113:
==== handshaking ====
==== Handshaking ====
Devices can only send the '''handshaking''' to host when the host isn't sending data. New devices doesn't has any '''origin''' address yet thus the origin, in the header message field, must contain the '''0x00''' value. Once that host received the '''handshaking''' it will generate an address to new device, this address value must be between 0x80 and 0xFF, inclusively, and must be informed to device using the '''destination''' field. The '''data''' field of original message must be give back to device untouched.
Devices can only send the '''handshaking''' to host when the host isn't sending data. New devices doesn't have any '''origin''' address yet thus the origin, in the header message field, must contain the '''0x00''' value. Once that host received the '''handshaking''' it will generate an address to new device, this address value must be between 0x80 and 0xFF, inclusively, and must be informed to device using the '''destination''' field. The '''data''' field of original message must be given back to device untouched, allowing the device discover its address.
The '''channel''' field is used to differentiate devices of the same type, i.e. same device URI. Each device can choose its own way to select the channel.
Line 134: Line 145:
==== device descriptor ====
==== Device descriptor ====
The '''device descriptor''' should contain all information about the actuators of the device. The host can optionally request the device descriptor of the device. Actually, only devices unknown by host need to be requested.
''host to device''
''host to device'' data field
Line 146: Line 159:
''device to host''
''device to host'' data field
Line 196: Line 209:
| rowspan="4" | modes list
| rowspan="3" | mode 1
| mask 1
| relevant
| property mask 1
| relevant (mask 1)
| 1
| 1
| mask 2
| mandatory
| property mask 2
| mandatory (mask 2)
| 1B_str
| 1B_str
Line 213: Line 226:
| 1
| 1
| slots
| max assignments
Line 248: Line 261:
==== control assignment ====
The '''actuator id''' is number defined by device developer used as short way to indentify an actuator of the device.
Some devices developers can like to have a stacking assignment feature, which would be possible to have more than one assignment to same actuator. This have to be defined on the field '''max assignments'''. Using max assignments greater than one is possible, for example, use a button to navigate through of the assignments.
The '''steps list''' contains the values of steps that the device developer recommends to be used with that actuator.
The '''modes''' describe to the host the LV2 properties supported by the actuator. Each mode is composed by two masks and one label. Each bit of each mask represents one LV2 control property. The first mask, the '''relevant''', it's used to define if the bits of '''mandatory''' mask has to be evaluated.
The '''label''' of mode is a friendly name to help the user understand what the mode does.
The masks structure is:
! bit 7
! bit 6
! bit 5
! bit 4
! bit 3
! bit 2
! bit 1
! bit 0
| integer
| logarithmic
| toggled
| trigger
| scale points
| enumeration
| tap tempo
| bypass
Example:
! style="text-align: center; font-weight: bold;" | mode
! style="font-weight: bold;" | mask
! style="font-weight: bold;" | integer
! style="font-weight: bold;" | logarithmic
! style="font-weight: bold;" | toggled
! style="font-weight: bold;" | trigger
! style="font-weight: bold;" | scale points
! style="font-weight: bold;" | enumeration
! style="font-weight: bold;" | tap tempo
! style="font-weight: bold;" | bypass
| rowspan="2" | ON/OFF
| relevant
| style="text-align: center;" | 0
| style="text-align: center;" | 1
| mandatory
| rowspan="2" | PULSE
| relevant
| mandatory
! style="font-weight: bold;" | mask value
| relevant
| style="text-align: center;" | 0x7F
| mandatory
| style="text-align: center;" | 0x20
| rowspan="2" | PULSE
| relevant
| mandatory
| style="text-align: center;" | 0x30
| rowspan="2" | TAP TEMPO
| relevant
| style="text-align: center;" | 0xFF
| mandatory
| style="text-align: center;" | 0x02
| rowspan="2" | ENUMERATION
| relevant
| mandatory
| style="text-align: center;" | 0x0C
* ON/OFF if '''toggled''' is implemented but not '''logarithm''', '''trigger''', '''scale points''', '''enumeration''' and '''tap tempo'''. '''integer''' is irrelevant.
* PULSE if '''toggled''' AND '''trigger''' are implemented but not '''logarithm''', '''scale points''', '''enumeration''' and '''tap tempo'''. '''integer''' is irrelevant.
* TAP TEMPO if '''tap tempo''' is implemented and no other.
* ENUMERATION if '''enumeration''' AND '''scale points''' are implemented but not '''logarithm''', '''toggled''', '''trigger''' e '''tap tempo'''. '''integer''' is irrelevant.
==== Control assignment ====
The device will receive this command when the user assing a control to one of your actuators. The device must reply with a '''error code''' indicating whether was possible assigned the requested control to the actuator.
''host to device''
''host to device''
Line 279: Line 500:
| rowspan="2" | chosen mode
| 1
| 1
| mask 1
| relevant
| mask 1 of chosen mode
| relevant (mask 1) of chosen mode
| 1
| 1
| mask 2
| mandatory
| mask 2 of chosen mode
| mandatory (mask 2) of chosen mode
| label
| label
Line 351: Line 572:
''device to host''
''device to host''
Line 360: Line 580:
! description
! description
| response status
| error code
| 2
| 1
| indicates whether assignment was well done
==== data request ====
The '''assignment id''' is a number that is short way to reference the assignments. It's used in the '''data request''' and '''unassignment''' commands. The '''port mask''' field defines the LV2 control port properties, the mask use the same structure as presented in the [[#device descriptor|device descriptor]]. The '''chosen mode''' is used by device to indentify which of your modes has to be applied to this assignment.
The '''unit render''' is printf format string for rendering a value (eg. "%f dB"). The fields '''value''', '''minimum''', '''maximum''', '''default''' and the '''value''' of '''scale points''' use the float standard IEEE 754.
==== Data request ====
This command is used to ask data of the devices. The host send '''data request''' to device and the devices must always send a response back to the host.
Preferably, the response should have only the values of the modified actuators.
''host to device''
! field
! field
! size
! size
! description
| sequence
| [none]
| 1
| 0
| sequential number used to detect non answered messages
''device to host''
Line 411: Line 635:
==== control unassignment ====
The '''value''' uses the float standard IEEE 754.
==== Control unassignment ====
''host to device''
''host to device''
Line 435: Line 663:
==== error report ====
==== Error report ====
''host to device or device to host''
Line 461: Line 689:
Initially host is waiting for devices handshaking, once the first device sends the handshaking, the host must response back informing its ''device id'' in the destination field. After that host can request the device descriptor and wait for device response or timeout. Since the device is identified on host, it should wait until the host send to it an assignment request.
The host start to polling the identified devices for data request as soon as an assignement is done. The polling period is determinated by the host considering the count of identified devices. In each polling devices cycle the host is responsible to reserve a short period of time to allow that new devices connect to it or send other requests, this because devices can only send messages to host when it isn't sending any message.
== See also ==
The host can control when the devices will message it keeping its transmission line sending data.
* [http://lv2plug.in/ns/ lv2 specifications]
* [http://lv2plug.in/ns/lv2core/#integer lv2 integer]
* [http://lv2plug.in/ns/ext/port-props/#logarithmic lv2 logarithmic]
* [http://lv2plug.in/ns/lv2core/#toggled lv2 toggled]
* [http://lv2plug.in/ns/ext/port-props/#trigger lv2 trigger]
* [http://lv2plug.in/ns/lv2core/#ScalePoint lv2 scale points]
* [http://lv2plug.in/ns/lv2core/#enumeration lv2 enumeration]
About
Physical interface
Protocol
Message Structure
field size
header 6
data N
Expanding the fields:
field subfield size
header destination 1
origin 1
command 1
data size 2
check 1
data data 0 1
data 1 1
... N
0x05 h e l l o
Commands
The valid commands are:
value description
0x01 handshaking
0x02 device descriptor
0x03 control assignment
0x04 data request
0x05 control unassignment
0xFF error report
Handshaking
field size description
device URI 1B_str a string that identifies the device
channel 1 channel configured on device
protocol version (major) 1 major number version control
protocol version (minor) 1 minor number version control
Device descriptor
field size
[none] 0
device to host data field
field size subfield 1 subfield 2 subfield 3 subfield 4 description
device label 1B_str friendly device name
actuators count 1 amount of actuators of the device
actuators list 1 actuator 1 id actuator id
1B_str name actuator name
1 modes count amount of supported assignment modes
1 modes list mode 1 relevant relevant (mask 1)
1 mandatory mandatory (mask 2)
1B_str label mode label
1 max assignments amount of controls that can be assigned to this actuator
1 steps count amount of values in the steps list
2 steps list value 1 step value 1
2 value 2 step value 2
bit 7 bit 6 bit 5 bit 4 bit 3 bit 2 bit 1 bit 0
integer logarithmic toggled trigger scale points enumeration tap tempo bypass
Example:
mode mask integer logarithmic toggled trigger scale points enumeration tap tempo bypass
ON/OFF relevant 0 0 1 1 0 0 0 0
mandatory 0 0 1 0 0 0 0 0
PULSE relevant 0 0 1 1 0 0 0 0
mandatory 0 0 1 1 0 0 0 0
mode mask integer logarithmic toggled trigger scale points enumeration tap tempo bypass mask value
ON/OFF relevant 0 1 1 1 1 1 1 1 0x7F
mandatory 0 0 1 0 0 0 0 0 0x20
PULSE relevant 0 1 1 1 1 1 1 1 0x7F
mandatory 0 0 1 1 0 0 0 0 0x30
TAP TEMPO relevant 1 1 1 1 1 1 1 1 0xFF
mandatory 0 0 0 0 0 0 1 0 0x02
ENUMERATION relevant 0 1 1 1 1 1 1 1 0x7F
mandatory 0 0 0 0 1 1 0 0 0x0C
  • ON/OFF if toggled is implemented but not logarithm, trigger, scale points, enumeration and tap tempo. integer is irrelevant.
  • PULSE if toggled AND trigger are implemented but not logarithm, scale points, enumeration and tap tempo. integer is irrelevant.
  • TAP TEMPO if tap tempo is implemented and no other.
  • ENUMERATION if enumeration AND scale points are implemented but not logarithm, toggled, trigger e tap tempo. integer is irrelevant.
Control assignment
host to device
field size subfield 1 subfield 2 description
actuator id 1 actuator identifier
assignment id 1 assignment identifier
port mask 1 LV2 control port properties
chosen mode 1 relevant relevant (mask 1) of chosen mode
1 mandatory mandatory (mask 2) of chosen mode
label 1B_str control label
value 4 current control value
minimum 4 minimum control value
maximum 4 maximum control value
default 4 default control value
step 2 control step
unit render 1B_str control unit reder
scale points count 1 amount of control scale points
scale points list 1B_str scale point 1 label scale point label
4 value scale point value
device to host
error code 1 indicates whether assignment was well done
Data request
field size
[none] 0
assignments count 1 amount of assignments in the list
assignments list 1 assignment 1 id assignment identifier
4 value current assignment value
host to device
device to host
field size
[none] 0
Error report
error on command 1 indicates which command raise the error
error code 1 a number that represents the error
error message 1B_str string that describes the error
Operation
See also
